Hello all!
First time poster here but longtime fan of this forum.
I have a 200amp, main breaker, exterior panel on an existing home. We are in the process of re-wiring entire house to get rid of all cloth wiring. Anyway, we will have a new 100-amp sub-panel that will feed off the original 200. It will serve the kitchen and laundry room. The calculated load of sub-panel came out to be 80 amps. The service cable will be approximately a 15-foot run. That said, was I wrong in using "83% rule"? I submitted a drawing to local municipality showing a #2 Al SER cable feeding said panel and it was accepted. The more a think about it though, I believe it may incorrect since the panel will not be carrying the entire load of residence as stated in 310.15(B)(7).
Any input would be much appreciated.
Thank You!
Ted
First time poster here but longtime fan of this forum.
I have a 200amp, main breaker, exterior panel on an existing home. We are in the process of re-wiring entire house to get rid of all cloth wiring. Anyway, we will have a new 100-amp sub-panel that will feed off the original 200. It will serve the kitchen and laundry room. The calculated load of sub-panel came out to be 80 amps. The service cable will be approximately a 15-foot run. That said, was I wrong in using "83% rule"? I submitted a drawing to local municipality showing a #2 Al SER cable feeding said panel and it was accepted. The more a think about it though, I believe it may incorrect since the panel will not be carrying the entire load of residence as stated in 310.15(B)(7).
Any input would be much appreciated.
Thank You!
Ted