310.15b16. Voltage drop/terminal ratings

Status
Not open for further replies.

Danny89

Member
Location
Indian Land
Can someone explain the answer to this example with code tables and notes. Formula for voltage drop is three phase

Chapter 9 table 8 is where u get the circular mils size for wire. Cooper think wire is to be used.

Terminal ratings are 75 degrees Celsius.

3 hots 1 ground needed 100amp load. 500feet away. What size wire is needed?
Thanks in advance

Sent from my Moto Z (2) using Tapatalk
 
Sounds like a home work question (without enough information) so take a shot at it and give us your answer first.

Roger
 
Voltage is missing. (Both from the question, and the far end of the wire)

Sent from my SM-G950U using Tapatalk

The actual voltage drop wold be the same regardless. Obviously the % drop would change.
 
The actual voltage drop wold be the same regardless. Obviously the % drop would change.
Which effects the size of the conductor. He's looking for a wire size. I was taught to look at the starting voltage when using a voltage drop formula to size wires.

Sent from my SM-G950U using Tapatalk
 
Which effects the size of the conductor. He's looking for a wire size. I was taught to look at the starting voltage when using a voltage drop formula to size wires.

Sent from my SM-G950U using Tapatalk
my apology.. when I read it I thought he was just looking for the voltage drop.
 
my apology...

Whew...lol. i thought for a second there i was going to have yet another guy on this forum tell me the way i do things is wrong.

I hope the OP gives us the info we want so everyone can chime in with how they would go about sizing this one.

Sent from my SM-G950U using Tapatalk
 
Well, he said 3 phase, 100 amps... so that starts around what, number 2... copper thhn is what I am assuming cooper think means but...of course, now you have the three conductors in a tray or such so you have derating and the 500 feet with 75 degree connections....2/0?.
 
Well, he said 3 phase, 100 amps... so that starts around what, number 2... copper thhn is what I am assuming cooper think means but...of course, now you have the three conductors in a tray or such so you have derating and the 500 feet with 75 degree connections....2/0?.
If only 3 conductors there is no adjustment necessary. 3AWG is good for 100 amps 75C.

What is not real clear is if the load is 100 amps or if it a 100 amp feeder with a lesser load on it, as well as what is continuous, what is non continuous for load. Once one knows absolute minimum conductor needed then comes how much voltage drop is acceptable and can the minimum ampacity conductor provide that or not.
 
Question is...
100a load not continuous. 75 degrees Celsius terminal ratings. 3 phase 480volt supply. 450 feet distance. What size wire should be used?

Answer is:
1.732x12.9x100x450/14.4=69,821.25 cmils

Chapter 9 table 8 ...#1 awg will work ...83,690 cmils. Copper

Sent from my Moto Z (2) using Tapatalk
 
Question is...
100a load not continuous. 75 degrees Celsius terminal ratings. 3 phase 480volt supply. 450 feet distance. What size wire should be used?

Answer is:
1.732x12.9x100x450/14.4=69,821.25 cmils

Chapter 9 table 8 ...#1 awg will work ...83,690 cmils. Copper

Sent from my Moto Z (2) using Tapatalk
You didn't mention acceptable voltage drop in the question, but apparently is 14.4 volts.
 