310.15b16

Djelite

Senior Member
Location
Ny
Occupation
Electrician
The 90 degree column is used for ampacity of conductors. Does that apply to all conductors when you’re dealing with ampacity adjustments and corrections? Or due some conductors get adjusted to the 75 degree when dealing with ampacity?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
If the conductors are 90° C conductors (THHN for example) you would use the 90° C ampacity for the adjustments. If you had a 75° C conductor like THWN then you would use the 75° C ampacity.
 