310.16 (4) (a)... when is the neutral carrying anything other than the unbalanced load? :-?
Bobhook149 Senior Member Aug 13, 2009 #1 310.16 (4) (a)... when is the neutral carrying anything other than the unbalanced load? :-?
S SEO Senior Member Location Michigan Aug 13, 2009 #2 Section 310.15 (4) (a). In a two wire circuit it carries the full load.
LarryFine Master Electrician Electric Contractor Richmond VA Location Henrico County, VA Occupation Electrical Contractor Aug 13, 2009 #3 Bobhook149 said: ... when is the neutral carrying anything other than the unbalanced load? :-? Click to expand... Another example: a 3-wire (2-hots and the neutral) 120/208v circuit from a Y panel.
Bobhook149 said: ... when is the neutral carrying anything other than the unbalanced load? :-? Click to expand... Another example: a 3-wire (2-hots and the neutral) 120/208v circuit from a Y panel.