If you give some examples of what you are trying to understand you can get more specific responses.
What Rob said is exactly correct. What Rob didn't mention is that you can use the 90c column when you are derating conductors but the final ampacity calculation cannot exceed the column that your terminations or wiring methods restrict you to.
It depends on the wiring method, the conductor insulation and the temperature ratings of the connections. For NM cable you would use the 60? C column. For THHN in conduit you would almost always use the 75? C column.
So you could use #4 copper THHN on a 90 amp breaker?
So you could use #4 copper THHN on a 90 amp breaker?
So you could use #4 copper THHN on a 90 amp breaker?
This may be a good replacement for the old method #2 AL was being used for in Resi. To feed all the branch circuits at the inside sub panel .
What is the correct way to read this table. How do you know which column to use. Thanks I've been getting a lot of different answers.
These columns just specify the current carrying capacity based on temperature and insulation type.
It sure takes some getting used to.![]()
if you are under 100amps and under #4 then you use 60deg column, if you are over those specs then 75deg. column. but their is alot more to that table.