C cyriousn Senior Member Location ME / CT Occupation EE & BIM Feb 20, 2025 #1 Does anyone know if 311.12 applies to overhead ACSR cables? It's technically a conductor so I'm thinking it does apply. Thanks all.
Does anyone know if 311.12 applies to overhead ACSR cables? It's technically a conductor so I'm thinking it does apply. Thanks all.
E Elect117 Senior Member Location California Occupation Engineer E.E. P.E. Feb 20, 2025 #2 I would think so. There is the, "unless specified elsewhere in the code" part but I can't think of any other sections would apply.