buck33k
Senior Member
- Location
- Washington state and North Carolina
I've been in the archives and on a couple of equipment manufacturers websites and I'm abit disappointed to find that most, if not all, sealing locknuts are listed only for RMC and IMC.I would like to use them on 2" PVC terminal adapters to enter a raintite enclosure above the level of uninsulated live parts to comply with 312.2. (Specifically, out the back of a CT can above the CTs.)
I understand that there are o-rings that are UL approved made for this purpose but have never used them.
Are there sealing locknuts approved for rigid PVC conduit fittings?
Who makes the o-rings?
Thanks
Buck
I understand that there are o-rings that are UL approved made for this purpose but have never used them.
Are there sealing locknuts approved for rigid PVC conduit fittings?
Who makes the o-rings?
Thanks
Buck