wwhitney
Senior Member
- Location
- Berkeley, CA
- Occupation
- Retired
A hypothetical: say we have a cabinet, a raceway connected to it, and another enclosure at the end. So a complete raceway from enclosure to enclosure, not a sleeve. And for whatever reason we use the raceway to pull in a cable instead of individual conductors. The raceway is properly sized using the cable's equivalent circular area.
(1) For individual conductors, that would be the end of the story, with the conductors loose in the raceway and at the entrances to both enclosures, but does 312.5(C) require that the cable be secured to the cabinet? It doesn't have any language that I can see as an exception for the case of cable in conduit, it just says "Where cable is used, each cable shall be secured to the cabinet, cutout box, or meter socket enclosure." 312.5(C) exception is not material for this question, as it is a very specific allowance for a very specific geometry that is not met.
(2) If securing the cable to the cabinet is required, would a type 21S push mount cable tie suffice? Its use involves drilling a small (3/16" or 1/4") hole in the cabinet, pushing the mounting wings into the hole, and then the normal cable tie end:
Cheers, Wayne
PS Note that for Article 314 enclosures, I don't see any such issue in 314.17. For example, the last sentence of 314.17(B) on metal boxes says "Where raceway or cable is installed with metal boxes or conduit bodies, the raceway or cable shall be secured to such boxes and conduit bodies." Here it is reasonable to read the last "or" as meaning it is enough to secure either the raceway or the cable to the box, no need to secure both.
(1) For individual conductors, that would be the end of the story, with the conductors loose in the raceway and at the entrances to both enclosures, but does 312.5(C) require that the cable be secured to the cabinet? It doesn't have any language that I can see as an exception for the case of cable in conduit, it just says "Where cable is used, each cable shall be secured to the cabinet, cutout box, or meter socket enclosure." 312.5(C) exception is not material for this question, as it is a very specific allowance for a very specific geometry that is not met.
(2) If securing the cable to the cabinet is required, would a type 21S push mount cable tie suffice? Its use involves drilling a small (3/16" or 1/4") hole in the cabinet, pushing the mounting wings into the hole, and then the normal cable tie end:
Cheers, Wayne
PS Note that for Article 314 enclosures, I don't see any such issue in 314.17. For example, the last sentence of 314.17(B) on metal boxes says "Where raceway or cable is installed with metal boxes or conduit bodies, the raceway or cable shall be secured to such boxes and conduit bodies." Here it is reasonable to read the last "or" as meaning it is enough to secure either the raceway or the cable to the box, no need to secure both.