I don’t quite understand this chart. For example if I have single conductor 500kCMIL 600V, XHHW-2, bottom feed into a switchgear base plate with lugs (removable type straight in) vendor provided it appears I only need 14” of vertical space? Or does the 14” refer to bending space?


Sent from my iPhone using Tapatalk
 

tortuga

Code Historian
Location
Oregon
Occupation
Electrical Design
Yes and Its bending space, see Note 1 at the bottom of the table and 312.6(B)(2)
and keep 312.7 in mind.
 