jim k
Member
- Location
- Northwestern Oregon
312.8 Enclosures for Switches or Overcurrent Devices. Enclosures for switches or overcurrent devices shall not be used as junction boxes, auxiliary gutters, or raceways for conductors feeding through or tapping off to other switches or overcurrent devices, unless adequate space for this purpose is provided. The conductors shall not fill the wiring space at any cross section to more than 40 percent of the cross-sectional area of the space, and the conductors, splices, and taps shall not fill the wiring space at any cross section to more than 75 percent of the cross-sectional area of that space.
My question has to do with the phrase ?adequate space for this purpose? and specifically the words, ?for this purpose.?
As I understand it, the section is talking about wires that enter an enclosure and then exit it without landing on, let?s say, a breaker within the enclosure. It admonishes us not to do this unless there?s ?adequate space for this purpose.? I interpret this to mean that such wires have to be placed in those areas of the enclosure that are meant to be wireways as opposed those spaces that are meant to contain the panel parts -- i.e. buses, breakers, mounting hardware, etc.
Another inspector insists that the section is more restrictive. His contention is that the only time ?feed through? wiring is allowed in a panel enclosure is when there?s a specific ?space for this purpose? (foreign wires). He cites the fact that UL 67 doesn?t include feed through wiring as part of the listing of this equipment. His common-sense argument is that someone might switch off power to a panel and reasonably assume that all conductors within the enclosure would then be de-energized ? a possibly fatal assumption. Since there are no panel enclosures that are so rated, the practice is never allowed.
If he's right, I've got to wonder why the section is so specific about the wire fill requirements toward the end.
What do you all think?
- Jim K