ptonsparky
Tom
- Occupation
- EC - retired
Working on a project that requires a 312.9 amp feeder. Previous EC in years past installed a buried paralleled set of 2/0 THWN cu with EG, one conduit. They had it fused @ 200 amp. I am guessing they were worried about VD. I am not. Using an ambient correction of 1.15 I can get roughly 322. FWIW Motor load, 3ph, 480v about 560' distance. 4 VFDs, plus some small across the line.
IIRC I am limited to the distance those wires can travel in a different ambient before I loose that 1.15 correction. I believe it was 6'. What is the NEC reference?
IIRC I am limited to the distance those wires can travel in a different ambient before I loose that 1.15 correction. I believe it was 6'. What is the NEC reference?