I've been arguing this section of code with another electrician and would appreciate any input that might clarify this section of the code.
314.23 (B)(1) states, "Nails and Screws. Nails and screws, where used as a fastening means, shall be attached by using brackets on the outside of the enclosure, or they shall pass through the interior within 6 mm (1/4") of the
back or ends of the enclosure."
Reading this literally, I take it to mean you cannot, for example, use screws through the holes in the back of a 4" square junction box to secure it to a joist. The "interior" of the box is the empty space within the sides and back of the box. A screw through the back of the box does not pass through the interior. It only passes through the material of the box itself.
Everyone does it. I've never seen an inspector tag it. Am I missing something here?
314.23 (B)(1) states, "Nails and Screws. Nails and screws, where used as a fastening means, shall be attached by using brackets on the outside of the enclosure, or they shall pass through the interior within 6 mm (1/4") of the
back or ends of the enclosure."
Reading this literally, I take it to mean you cannot, for example, use screws through the holes in the back of a 4" square junction box to secure it to a joist. The "interior" of the box is the empty space within the sides and back of the box. A screw through the back of the box does not pass through the interior. It only passes through the material of the box itself.