Comparing these two sections is confusing to me. Say I have a 1" RMC conduit running into a 1" trade size T condulet; one branch is 1", and the other branch is 3/4" branch (with a 1"-3/4" reducer). According to 344.30(A) I need a support within 3' of the T condulet for all three conduits. But if I look at 314.23(E), it seems I can use one support for all three conduits: one within 3' of the T and the other two conduit branches, i.e. 1" and 3/4", can be supported within 10 feet from the first support at 3' from the T. Thoughts?
 
I don't believe that a conduit body requires any support if the trade size is the same as the raceway due to the exception . Here's my thoughts on this in post #3.

 
Ok, but do you think a single support can be used within 3 feet of the trade size conduit body if all three branches are the same size? (No reducers). and the other two can be supported within 10' of the first support? thanks, Dale
 
Ok, but do you think a single support can be used within 3 feet of the trade size conduit body if all three branches are the same size? (No reducers). and the other two can be supported within 10' of the first support? thanks, Dale
Sure but IMO it's also not required because that code language doesn't exist when applying the exception. Thoughts?
 
Sure but IMO it's also not required because that code language doesn't exist when applying the exception. Thoughts?
You have a valid point, but if I consider 344.30(A) as the 'base rule', and support the trade size T within 3', then at 10', 12', 14' etc per T344.30(B)(2) for the other two, I believe it has a better chance of passing inspection.
My main concern is that each of the 3 conduits do not have to be supported within 3' of the T condulet - do you agree?
 
My main concern is that each of the 3 conduits do not have to be supported within 3' of the T condulet - do you agree?
Yes I agree. If the standard 10' support rule for the raceway is followed additional supports at the conduit body are not required due to the exception. For example if I have a conduit on a rack with supports 10' apart I can cut in a C conduit body at 5' from either rack with no additional support as long as the CB is the same trade size as the raceway.
 
Assuming you are using RMC for this, I don't see how you can avoid strapping the RMC within 3' (or 5' if there isn't anything readily available for fastening ) Yes 3124.23 allows it. But there is no exception for 344.30(A)
 
Assuming you are using RMC for this, I don't see how you can avoid strapping the RMC within 3' (or 5' if there isn't anything readily available for fastening ) Yes 3124.23 allows it. But there is no exception for 344.30(A)

This is why it’s so confusing to me also - I tend to agree with you and OP


Enviado desde mi iPhone utilizando Tapatalk
 
Last edited:
Assuming you are using RMC for this, I don't see how you can avoid strapping the RMC within 3' (or 5' if there isn't anything readily available for fastening ) Yes 3124.23 allows it. But there is no exception for 344.30(A)
Everything in 314.23(E) overrides the general support rules including the exception for conduit bodies that are raceway supported. Personally I think the exception should be deleted from the code language.
 
Everything in 314.23(E) overrides the general support rules including the exception for conduit bodies that are raceway supported. Personally I think the exception should be deleted from the code language.

Infinity why do you say 314.23(E) overrides the base rule?


Enviado desde mi iPhone utilizando Tapatalk
 
Infinity why do you say 314.23(E) overrides the base rule?
The basic rule is that a conduit body or the box needs to be supported within 3'. In order to apply any of the provisions of 314.23(E) which allows the raceway to support a box or conduit body you need to override the basic 3' support rule. If 314.23(E) doesn't not provide an exception to the basic 3' support rule then the wording is useless.
 
314.23(E) Exception does not provide any relief from the part of 314.23(E) that requires conduits to be secured within 3' of the enclosure. It just provides relief from the requirements about (a) the minimum of 2 conduit entries and (b) the maximum of 100 in^3 volume.

Moreover, 314.23(E) Exception can't possibly provide any relief from 344.30(A).

Cheers, Wayne
 
314.23(E) Exception does not provide any relief from the part of 314.23(E) that requires conduits to be secured within 3' of the enclosure. It just provides relief from the requirements about (a) the minimum of 2 conduit entries and (b) the maximum of 100 in^3 volume.

Moreover, 314.23(E) Exception can't possibly provide any relief from 344.30(A).

Cheers, Wayne
I mentioned box when I shouldn't have since this question is about conduit bodies. For a conduit supported box with threaded entries I can see the requirement for the raceway to be supported within 3'. That would not be required for conduit bodies of the same trade size as the raceways.
 
For a conduit supported box with threaded entries I can see the requirement for the raceway to be supported within 3'. That would not be required for conduit bodies of the same trade size as the raceways.
For a conduit body, it is required for each of the 5 conduit types listed in 314.23(E) Exception:

1) IMC -- 342.30(A)(1)
2) RMC -- 344.30(A)(1)
3) PVC -- 352.30(A)
4) RTRC -- 355.30(A) (although this one allows for conduit to be listed for a greater distance than 3')
5) EMT -- 358.30(A)(2) (although there is an allowance for fishing in finished buildings).

This is true whether or not 314.23(E) would require it; Article 314 can not amend the above Articles.

I also would say that 314.23(E) Exception is an exception only to the number of required conduit entries and the maximum 100 in^3 volume, and does not provide an exception to the 314.23(E) requirement for securing within 3' of the enclosure. A conduit body is an enclosure.

Cheers, Wayne
 
Wayne and Infinity. Going back to the T condulet scenario and 314.23(E):
Say we have a trade size 1” RMC T, that has 3, 3/4” RMC conduit (all 3 with 1”-3/4”reducers) would require a support within 3’ on EACH of the 3 conduits. However if we have a 1” T, with 3, 1” conduits at least one conduit support would be required within 3’ of the condulet since the base rule, ie 344.30 cannot be overridden by 314.23(E) Exception. Does this sound right?
 
However if we have a 1” T, with 3, 1” conduits at least one conduit support would be required within 3’ of the condulet since the base rule, ie 344.30 cannot be overridden by 314.23(E) Exception
344.30(A)(1) requires each conduit connected to the conduit body to be secured within 3' of the conduit body, regardless of what Article 314 says.

334.30 is about securing and supporting the conduit itself; 314.23 is about securing and supporting the conduit body. Two separate topics. The only relationship between them is that 314.23(E) says that when the conduit itself is properly supported, sometimes you can forgo supporting the conduit body directly.

Cheers, Wayne
 
344.30(A)(1) requires each conduit connected to the conduit body to be secured within 3' of the conduit body, regardless of what Article 314 says.

334.30 is about securing and supporting the conduit itself; 314.23 is about securing and supporting the conduit body. Two separate topics. The only relationship between them is that 314.23(E) says that when the conduit itself is properly supported, sometimes you can forgo supporting the conduit body directly.

Cheers, Wayne
I’ve never seen a conduit body itself being supported. You’d have to drill into the body and attach it with screws/bolts?
 
I’ve never seen a conduit body itself being supported. You’d have to drill into the body and attach it with screws/bolts?
Good question, maybe there is a more clever way to do it, but that would work. And for your example of "a trade size 1” RMC T, that has 3, 3/4” RMC conduit (all 3 with 1”-3/4”reducers)," you certainly have to secure the conduit body itself, as 314.23(E) Exception does not apply.

You could instead use a short length of 1" conduit into one of the conduit body entries, with a reducing coupling to 3/4" at the other end. Then 314.23(E) Exception does apply, and you just need to secure each of the conduits, including the 1", within 3' of the T.