I have a 480v, 20A, 3 phase, lighting circuit - each fixture is 277V. A 2" conduit runs the length of the entire lighting layout, with junction boxes (12"x12"x6") located at each fixture to tap one of the hots, neutral, and ground, with the fixtures alternating even between phase A, B, and C and running 3/4" flex conduit to each fixture. Due to large voltage drop calculations, the 5 wires (A,B,C, N, G) are #2 AWG running the length of the lighting circuit, with taps/splice at each box to #10 AWG down to the fixture.
This is where the disagreements begin:
Contractor is saying:
1) The installation is against code (NEC 2017) because it should be an 8x the largest raceway and should be 16" long because 2 of the 5 wires are not being spliced in each box, despite being part of the same circuit.
2) The "splice" is not really a splice because they're using insulation piercing connections - therefore it's a straight pull.
Questions:
1) If a 3 phase circuit has 3 of it's 5 wires tapped in each box, would it be treated as a straight pull box (8x) or splice box (6x)?
2) Is the insulation piercing connection not considered a splice?
My thoughts/interpretations:
1) Because it's a single circuit, it's a splice box, not a straight pull. If it were multiple circuits where one entire circuit just passed directly through the box, then it'd be a straight pull box calculation.
2) There's not a definition for splice in Article 100, but 110.14(B) Splices mentions "conductors shall be spliced or joined with splicing devices identified for the use.." (i.e. insulation piercing kits)
3) If the box should be a straight box, which I disagree, the box still meets code by way of 314.28(A)(3): 5#2 AWG wires takes up .59in2 which per the tables of Chapter 9, mean in theory we could have installed a 1 1/4" conduit instead of 2" and 1.25" x 8 = 10" and a 12" long box would be code compliant - am I interpreting that section correctly?
Thanks in advance code gurus!
This is where the disagreements begin:
Contractor is saying:
1) The installation is against code (NEC 2017) because it should be an 8x the largest raceway and should be 16" long because 2 of the 5 wires are not being spliced in each box, despite being part of the same circuit.
2) The "splice" is not really a splice because they're using insulation piercing connections - therefore it's a straight pull.
Questions:
1) If a 3 phase circuit has 3 of it's 5 wires tapped in each box, would it be treated as a straight pull box (8x) or splice box (6x)?
2) Is the insulation piercing connection not considered a splice?
My thoughts/interpretations:
1) Because it's a single circuit, it's a splice box, not a straight pull. If it were multiple circuits where one entire circuit just passed directly through the box, then it'd be a straight pull box calculation.
2) There's not a definition for splice in Article 100, but 110.14(B) Splices mentions "conductors shall be spliced or joined with splicing devices identified for the use.." (i.e. insulation piercing kits)
3) If the box should be a straight box, which I disagree, the box still meets code by way of 314.28(A)(3): 5#2 AWG wires takes up .59in2 which per the tables of Chapter 9, mean in theory we could have installed a 1 1/4" conduit instead of 2" and 1.25" x 8 = 10" and a 12" long box would be code compliant - am I interpreting that section correctly?
Thanks in advance code gurus!