In the dated MH slide below Dimension "A" shows as being 18" based on the (1) 3" entering the right hand wall. 314.28 states "The distance between raceway entries enclosing thesame conductor shall not be less than six times the metric designator (trade size) of the larger raceway" in which case the 18" would not provide enough distance to provide 6X the distance between raceways. Does the quoted section not apply since the conductors are spliced and not necessarily the "same conductor" ?