C codester New member Mar 18, 2005 #1 armored cable is permitted to be used with nonmetallic boxes if an internal bonding means is provided in each box. What constitutes an internal bonding means?
armored cable is permitted to be used with nonmetallic boxes if an internal bonding means is provided in each box. What constitutes an internal bonding means?
B bphgravity Senior Member Location Florida Mar 18, 2005 #2 Re: 314.3 exception 1 A way to attach a bonding jumper from the EGC to the metallic entries.
A allenwayne Senior Member Mar 18, 2005 #3 Re: 314.3 exception 1 That would be a migb bushing Boy talk about taking up space