Couple of years ago customer had a 320 Amp service installed on side of shop building with the intention of servicing the shop with one 200 Amp panel and the option to add another 200 Amp panel to a separate future home structure. Forward to now home construction is starting and I’m looking at this and have some questions about the setup. Currently the shop has a 200 Amp with main breaker set on the back of the meter base inside shop. Meter base has second set of service entrance conductors going to a 200 Amp breaker set beside meter base. See picture customer provided from initial install.
Because there is an OCPD, I assume the conductors running to the 2nd panel to be located in the house are no longer service conductors but are feeders requiring a 4-wire feed. If this is the case where does the EGC run? To the bonded panel 1 EGC? Does this leave me with a disconnect grouping situation?
I understand what the original intent was but would it be better to propose to remove the OCPD and run a 3-wire service entrance feed to the 2nd panel? House is 200 feet away by the way.
Because there is an OCPD, I assume the conductors running to the 2nd panel to be located in the house are no longer service conductors but are feeders requiring a 4-wire feed. If this is the case where does the EGC run? To the bonded panel 1 EGC? Does this leave me with a disconnect grouping situation?
I understand what the original intent was but would it be better to propose to remove the OCPD and run a 3-wire service entrance feed to the 2nd panel? House is 200 feet away by the way.