Re: 320 Amp Single Position Meter Socket
It's great for resi services where a 40 space panel (200A) is not quite big enough. You can put 2 panels next to each other and run both service entrance conductors to the load lugs of the meter pedestal. The lugs are rated for 2 conductors!
I commercial work same situation applies. "Generally" a 200 Amp panel isn't loaded up to 200A, for obvious reasons. If you can load it to 160 and have the other panel loaded at 160 the 320 meter socket pedestal works great.
You can size your conductors at 3/0 for each 200Amp panel. You could even install 2-100Amp panels and install #3 to each.
If I was going to use a single main, I would probably use a 400A switch and use the fuses for the calculated load. edit Not to exceed 320
edit:
Just checked specs on the meter--per manufacturer:
These units have a maximum continuous rating of 320 Amperes which must not be exceeded.
[ March 22, 2005, 04:03 PM: Message edited by: tshea ]