I was wanting to make sure I was figuring this right. I have a 3 phase 320 Meter can with a 3" rigid riser with 3-500mcm and 1-350 mcm conductors. My total load calculation is 320A. By code i can go down to these 500 mcm conductors as long as toal load does not exceed 380A. Is this a correct install. Also has anyone installed parallel 2" for the primary side of meter can. I know meter can comes with a single hole for a hub, but was wanting to see if anyone has installed a myers hub for second conduit. Would this be legal per code.
Thanks