Im bidding a new construction house with a 320 pedestal service. Give or take 150ft from the house. Correct me if I'm wrong.
The pedestal will have a 320 amp meter socket and (2) -200 amp main breaker disconnects.
(2) - 2" Seperate conduits from each disconnect to the house.
Do I still need 2 disconnects on the house or can the conduit go straight inside to the (2) 200 amp main breaker panels.
I will also need two ground rods at the pedestal and a ufer Ground (if available) at the house?
Water bond would be sized the conductors of the sub feeds? so a #4 copper would be fine?