320amp residential overhead service

Status
Not open for further replies.

difowler1

Senior Member
I have never installed an overhead 320amp service. All the 320amp services I have installed have been underground. I have the service mast needing to be 2 1/2" rigid pipe. With the wires for the service mast at 400kcmil copper conductors. Could I reduce the size of the neutral? Did I get it all wrong? They are planning to increase the load on house with a future swim pool and jacuzzi, and possibly more, so I figured to do the wiring at the whole 320amps.
 
Seems a little off,
3” conduit with 3-500mcm copper I believe what is needed and yes you could reduce neutral which may take you back to 2 1/2”
Unless you have load calculations which would prove otherwise.
 
320amp overhead service

320amp overhead service

I just installed one today for a commercial building. 2 - 500 MCM CU and 1 - 350 MCM CU in a 2 1/2" rigid riser. Split out to 2 200 amp disconnects. One was back to back and one extended.

Are you using the 60 degree Celsius column of 310.15(b)(16) to get the 500mcm? On 310-15(b)(7) (single phase dwelling services and feeders) for residential you can reduce the size of the wire to 83% of the service rating. So using that 60 degree column at 83%, I could use 300mcm?
 
Are you using the 60 degree Celsius column of 310.15(b)(16) to get the 500mcm? On 310-15(b)(7) (single phase dwelling services and feeders) for residential you can reduce the size of the wire to 83% of the service rating. So using that 60 degree column at 83%, I could use 300mcm?

No, I spaced out.

400kcmil is good for 335A. The load is 400A, so 400A x .83 = 332A.

You are over by 3A, not short. My bad.
 
I've never installed anything larger than a 200A service. What would a 320A service with two 200A panels cost the customer, on average, compared to a single 200A service. Let's say, for example, a 200A runs $1500 complete.
 