Section and Paragraph
330.30 (C)
Proposal Recommends
Revise text
Proposal
(C) Supporting. Unless otherwise provided, cables shall be supported at intervals not exceeding 1.8-m (6-ft)
Horizontal runs of Type MC cable installed in wooden or metal framing members or similar supporting means shall be considered supported and secured where such support does not exceed 1.8-m (6-ft) intervals.
Statement of Problem and Substantiation
As outlined in 320.30 type AC cable is not required to be secured when installed in horizontal runs through framing members.
Ie: (C) Supporting. Unless otherwise provided, Type AC cable shall be supported at intervals not exceeding 1.4 m (4? ft).
Horizontal runs of Type AC cable installed in wooden or metal framing members or similar supporting means shall be considered supported where such support does not exceed 1.4-m (4?-ft) intervals.
330.30 (C)
Proposal Recommends
Revise text
Proposal
(C) Supporting. Unless otherwise provided, cables shall be supported at intervals not exceeding 1.8-m (6-ft)
Horizontal runs of Type MC cable installed in wooden or metal framing members or similar supporting means shall be considered supported and secured where such support does not exceed 1.8-m (6-ft) intervals.
Statement of Problem and Substantiation
As outlined in 320.30 type AC cable is not required to be secured when installed in horizontal runs through framing members.
Ie: (C) Supporting. Unless otherwise provided, Type AC cable shall be supported at intervals not exceeding 1.4 m (4? ft).
Horizontal runs of Type AC cable installed in wooden or metal framing members or similar supporting means shall be considered supported where such support does not exceed 1.4-m (4?-ft) intervals.