330.30 (D,2)

Status
Not open for further replies.
I am installing typical "accessible" (t-bar) ceiling items (luminaires, occ sensors, etc.). My inspector is questioning the fact that I have no "support" within 12". (I have a support @ 4'-5')
He refers to 330.30 and says that 330.30(D,2) does not reference "secured" so he is enforcing that I supports the MC, flex within 12".

NEC does not have a definition of "secured" or "supported".

HELP
 

iwire

Moderator
Staff member
Location
Massachusetts
You are fine.

attachment.php
 

david luchini

Moderator
Staff member
Location
Connecticut
Occupation
Engineer
I am installing typical "accessible" (t-bar) ceiling items (luminaires, occ sensors, etc.). My inspector is questioning the fact that I have no "support" within 12". (I have a support @ 4'-5')
He refers to 330.30 and says that 330.30(D,2) does not reference "secured" so he is enforcing that I supports the MC, flex within 12".

NEC does not have a definition of "secured" or "supported".

HELP

Try 300.11 with regards to securing and supporting.
 