334.12 Uses Not Permitted.
(A) Types NM, NMC, and NMS. Types NM, NMC, and
NMS cables shall not be permitted as follows:
(2) Exposed in dropped or suspended ceilings in other than
one- and two-family and multifamily dwellings
334.15 Exposed Work. In exposed work,; except as
provided in 300. 11 (A), cable shall be installed as specified
in 334. 15(A) through (C).
(B) Protection from Physical Damage. Cable shall be
protected from physical damage where necessary by rigid
metal conduit, intermediate metal conduit, electrical
metallic tubing, Schedule 80 PVC rigid nonmetallic
conduit, or other approved means.
Good day all. Is running CAT5 (5e, 6, what have you) cable exposed in dropped ceilings a violation? I think so.
What are the "other approved means" available? I see CAT5 runs in cable trays in drop ceilings all the time. I understand that this was an addition in the 2005 cycle so older installations like this exist. Does a cable tray provide protection from physical damage in this case? I think the purpose of 334.12(A)(2) is to prevent cable from being damaged when someone tries to remove a ceiling panel; in such a case I'm think a cable tray would be adequate.
(A) Types NM, NMC, and NMS. Types NM, NMC, and
NMS cables shall not be permitted as follows:
(2) Exposed in dropped or suspended ceilings in other than
one- and two-family and multifamily dwellings
334.15 Exposed Work. In exposed work,; except as
provided in 300. 11 (A), cable shall be installed as specified
in 334. 15(A) through (C).
(B) Protection from Physical Damage. Cable shall be
protected from physical damage where necessary by rigid
metal conduit, intermediate metal conduit, electrical
metallic tubing, Schedule 80 PVC rigid nonmetallic
conduit, or other approved means.
Good day all. Is running CAT5 (5e, 6, what have you) cable exposed in dropped ceilings a violation? I think so.
What are the "other approved means" available? I see CAT5 runs in cable trays in drop ceilings all the time. I understand that this was an addition in the 2005 cycle so older installations like this exist. Does a cable tray provide protection from physical damage in this case? I think the purpose of 334.12(A)(2) is to prevent cable from being damaged when someone tries to remove a ceiling panel; in such a case I'm think a cable tray would be adequate.