goldstar
Senior Member
- Location
- New Jersey
- Occupation
- Electrical Contractor
I recent wired 2 new partitioned offices in a store that was converted from a hair salon to office space in a small strip mall. The original store was and wired by a local licensed electrician, inspected and was passed (not sure exactly how long ago but at least 10 years). The wiring above the suspended ceiling was done with NM cable. In fact, to the best of my knowledge, there isn't a piece of BX or MC in the entire strip mall, including the offices on the 2nd floor.
I was cited by the EI for installing NM cable above the ceiling (and rightfully so). I made the assumption that it was (or at least at one time was) Code compliant. All the wiring inside the partitioned walls was wired with NM cable and that was acceptable. That said, the EI offered several solutions to correcting the wiring problem :
Thanks in advance.
I was cited by the EI for installing NM cable above the ceiling (and rightfully so). I made the assumption that it was (or at least at one time was) Code compliant. All the wiring inside the partitioned walls was wired with NM cable and that was acceptable. That said, the EI offered several solutions to correcting the wiring problem :
- Replace all ceiling tiles with fire-rated tiles
- Where wiring enters the partitioned wall from the areas above the ceiling, sleeve that wiring in seal-tight
- Install a metal JB on top of the metal headers where the wiring enters the partition wall, install the NM cables there and splice in AC or MC cable to the points of origin or light fixtures.
Thanks in advance.