334.15(C)

Status
Not open for further replies.

gserve

Senior Member
Location
New Hampshire
In reference to 334.15(C) what is meant by "angles"? If I install a 4/O SER on the face or the studs in a straight line across the studs is this code compliant?
 

pierre

Senior Member
Re: 334.15(C)

Hello gserve

334.15(C) pertains to ceiling joists. If you were to install the wire at an 'angle', meaning not parallel with the joists. Also if you do install the SER on the face of studs, remember they have to be protected from physical damage and they will be compliant. While you are at it you might want to take a look at 320.23.

Pierre
 

bphgravity

Senior Member
Location
Florida
Re: 334.15(C)

Parallel to the joist would be a 0 degree angle. Completely perpendicular to the joist would be a 90 degree angle. Anything in between would be an "angle" to the member. :)
 