Old
334.15
(B) Protection from Physical Damage
[note: second paragraph]
Type NMC cable installed in shallow chases or grooves in masonry, concrete, or adobe, shall be protected in accordance with the requirements in 300.4(E) and covered with plaster, adobe, or similar finish.
New/Revision proposal
334.15
(B) Protection from Physical Damage
[note: second paragraph]
Type NMC cable installed in shallow chases or grooves in masonry, concrete, or adobe, shall be protected in accordance with the requirements in 300.4(F) and covered with plaster, adobe, or similar finish.
Substantiation: . When 330.4 was amended for the 2008 code cycle, this reference was not properly updated.
334.15
(B) Protection from Physical Damage
[note: second paragraph]
Type NMC cable installed in shallow chases or grooves in masonry, concrete, or adobe, shall be protected in accordance with the requirements in 300.4(E) and covered with plaster, adobe, or similar finish.
New/Revision proposal
334.15
(B) Protection from Physical Damage
[note: second paragraph]
Type NMC cable installed in shallow chases or grooves in masonry, concrete, or adobe, shall be protected in accordance with the requirements in 300.4(F) and covered with plaster, adobe, or similar finish.
Substantiation: . When 330.4 was amended for the 2008 code cycle, this reference was not properly updated.