lielec11
Senior Member
- Location
- Charlotte, NC
- Occupation
- Electrical Engineer (PE)
Part I
310.15(A)(3) dictates that the temperature rating of my cables are limited by the terminals of the equipment. It also says that most terminals are built for 60/75 DEG.
Early in my entire career I was taught to design for 75 DEG but specify 90 DEG on my drawings. Reading through this seems incorrect as most equipment isn't built for 90 DEG terminals. Is this correct, should I really be designing around 60 and specifying 75? Most other engineers seem to use the 75 DEG column as well, am I overthinking this?
Part II
338.80 limits the use of NM cable to the 60 degree column of Table 310.15(B)(16).
a) If I am specifying THHN or THWN cables in EMT am I beholden to the 60 DEG column or can I use the 75 DEG column?
b) What is stopping a contractor from using type NM (as long as it applies) in lieu of my specified THHN in EMT?
c) If that happens wouldn't the wire be undersized based on 338.80?
310.15(A)(3) dictates that the temperature rating of my cables are limited by the terminals of the equipment. It also says that most terminals are built for 60/75 DEG.
Early in my entire career I was taught to design for 75 DEG but specify 90 DEG on my drawings. Reading through this seems incorrect as most equipment isn't built for 90 DEG terminals. Is this correct, should I really be designing around 60 and specifying 75? Most other engineers seem to use the 75 DEG column as well, am I overthinking this?
Part II
338.80 limits the use of NM cable to the 60 degree column of Table 310.15(B)(16).
a) If I am specifying THHN or THWN cables in EMT am I beholden to the 60 DEG column or can I use the 75 DEG column?
b) What is stopping a contractor from using type NM (as long as it applies) in lieu of my specified THHN in EMT?
c) If that happens wouldn't the wire be undersized based on 338.80?