Massachusetts amended the 338.10(B)(4)(a)(3) in the NEC to state “Where installed in thermal insulation, the ampacity shall be in accordance with the 60 degree C (140 degree F) conductor temperature rating. The maximum conductor temperature rating shall be permitted to be used for ampacity adjustment and correction purposes, if the final derated ampacity does not exceed that for 60 degree (140 degree F) rated conductor“.
With this being said, I need to run some SE cable behind a wall with thermal insulation. I was thinking if I sleeve it in PVC where there is thermal insulation (About 15’) I could still use the SE cable at 75 degrees. Will that work in your opinion? Do I need to be concerned about heat dissipation sleeving it in PVC?
With this being said, I need to run some SE cable behind a wall with thermal insulation. I was thinking if I sleeve it in PVC where there is thermal insulation (About 15’) I could still use the SE cable at 75 degrees. Will that work in your opinion? Do I need to be concerned about heat dissipation sleeving it in PVC?