I have a 125mva transformer which has a 34.5 kv breaker on the secondary side which feeds a bus with other 34.5 kv breakers. The breaker has pt's and ground fault protection. It has no ct's for overcurrent protection for the buss feeding the other breakers. What protection should this line breaker have? The transformer is a delta to wye.
 

bob

Senior Member
Location
Alabama
Re: 34.5 kv breaker

Mike
Many time the ct's are built into the primary bushings. You should be able to open the control cabinet attached to the breaker and see the wiring to the ct's.
 

templdl

Senior Member
Location
Wisconsin
Re: 34.5 kv breaker

It is of my opinion that you don't mess with this gear. Equipment above 1000v is a whole other issue. Even CTs can be dangerous if they are open circuited. The best advise that I can give you is to hire someone who is qualified and understand this gear.
 

elmarea

Member
Location
upstate ny
Re: 34.5 kv breaker

What is the application for this equipment? Does this feed a large manufacturing plant?
I am assuming it is owned privately and not the local utility. This transformer is big!!

I am also curious as to why you are asking. If you are involved in designing, installing or updating the protection schemes, get professional help. If you are simply curious than here is some general information.

The protection schemes designed for this equipment may include any of the following; Transformer differential protection, Transformer overload protection, and/or bus differential protection.

The breaker itself would not have any protection, it would be used to protect other equipment such as the transformer or the equipment it is feeding.

The bus generally does not have overload protection because it would have been designed and built based on a short circuit study and capable of with standing current up to at least that amount. The transformer would be the limiting factor here.

Bus differential protection would monitor all the current entering and leaving the bus and trip all breakers attached to the bus whenever a discrepancy occurred.

A transformer this large may have a differential protection scheme fed by CT's on the high side transformer bushings and the low side bank breaker. However if the breaker does not have ct's than this clearly wasn't intended.

It would also have some type of overload protection scheme that could be as simple as fuses.

The list could go on and on but suffice it to say the package would be professionally designed with the big picture in mind.
 