Hi All,
I am new on this forum and have a question that I haven't been able to get answered elsewhere. With so much expertise hanging around this forum, I hope someone can help.
The electrical contractor on a job I am working on has done something that I find quite suspicious. On a portion of underground conduit (IMC), he joined two pieces of conduit with a standard threaded coupling plus a compression connector. OK, that probably would not be a problem, except he inserted the threaded end of the next piece of conduit into the slip side of the compression fitting.
Section 342.42(A) of the 2005 NEC states the following:
"Threadless couplings and connectors shall not be used on threaded conduit ends unless listed for the purpose."
Here's my question: Does anyone know of a manufacturer that makes a compression fitting listed for such an installation?
The electrician insists that this connection is even better than a plain slip fit, although he hasn't explained why he believes this. He has so far ignored my requests to provide the manufacturer and part number of the connector so I can verify if it is listed for use with the threaded end of conduit. I don't believe this fitting is going to have any chance of keeping water out of the conduit.
Any comments?
I am new on this forum and have a question that I haven't been able to get answered elsewhere. With so much expertise hanging around this forum, I hope someone can help.
The electrical contractor on a job I am working on has done something that I find quite suspicious. On a portion of underground conduit (IMC), he joined two pieces of conduit with a standard threaded coupling plus a compression connector. OK, that probably would not be a problem, except he inserted the threaded end of the next piece of conduit into the slip side of the compression fitting.
Section 342.42(A) of the 2005 NEC states the following:
"Threadless couplings and connectors shall not be used on threaded conduit ends unless listed for the purpose."
Here's my question: Does anyone know of a manufacturer that makes a compression fitting listed for such an installation?
The electrician insists that this connection is even better than a plain slip fit, although he hasn't explained why he believes this. He has so far ignored my requests to provide the manufacturer and part number of the connector so I can verify if it is listed for use with the threaded end of conduit. I don't believe this fitting is going to have any chance of keeping water out of the conduit.
Any comments?