Does this apply to all forms of conduit? FMC, FNMC etc..
H Hendrix Senior Member Location New England Jun 24, 2013 #1 Does this apply to all forms of conduit? FMC, FNMC etc..
E eprice Senior Member Location Utah Jun 24, 2013 #2 Hendrix said: Does this apply to all forms of conduit? FMC, FNMC etc.. Click to expand... 344.26 is in the article on RMC, and thus only applies to RMC. You need to look at each of the articles for the other forms of conduit for requirements that pertain to them. 348.26 applies to FMC, 356.26 applies to LFNC, etc.
Hendrix said: Does this apply to all forms of conduit? FMC, FNMC etc.. Click to expand... 344.26 is in the article on RMC, and thus only applies to RMC. You need to look at each of the articles for the other forms of conduit for requirements that pertain to them. 348.26 applies to FMC, 356.26 applies to LFNC, etc.
H Hendrix Senior Member Location New England Jun 25, 2013 #3 Other articles for conduit tells me that 360 is max for all.
ActionDave Chief Moderator Staff member Location Durango, CO, 10 h 20 min from the winged horses. Occupation Licensed Electrician Jun 26, 2013 #4 Hendrix said: Other articles for conduit tells me that 360 is max for all. Click to expand... That is correct.
Hendrix said: Other articles for conduit tells me that 360 is max for all. Click to expand... That is correct.