344.30(A) Securely fastened (not "supported") - RMC shall be secured in accordance with one of the following:
(1) - RMC shall be securely fastened within 3ft of each outlet box, junction box, device box, cabinet, conduit body, or other conduit termination.
(2) - Fastening shall be permitted to be increated to a distance of 5ft where structural members do not readily permit fastening within 3ft.
(3) - Where approved ... (deals with going through roof for mast)
how did you attach a CLI, DIVI box to strut without drilling a hole through it? to maintain the hazardous ratings of those enclosures, they could/should be supported by the conduits installed in them as permitted in 314.23(E) and have the conduit strapped to the strut, not the enclosure. after this, you're into distance restrictions on the distance from the box from 314.23, not 344.30.
no more than 3ft if conduits are on differing sides of the box, and 18 inches if the two pipes are on the same side of