hattrick72
Member
- Location
- Halifax, NS, Canada
Good day all,
I have a 347/600V generator and I will be connecting it to a 600V/208V delta to wye transformer. I do not know what random loads are going to be connected to the transformer so I must assume I will end up with some unbalanced phases. Is it perfectly okay to connect only my phases to the transformer and leave my neutral floating, or should I tie the neutral within my generator to the generator ground. The secondary of my transformer will have a neutral to ground bond with my main electrode in the vicinity of my transformer secondary. I will not be installing any other electrode in the system and I will also have a bond connecting to every panel board the system supplies. (This is a temporary set-up for a field exercise)
If I leave the neutral floating I will run a bond from my gen container to the transformer.
If I bond my neutral to ground at the generator I will be installing an electrode at the generator and bond my two electrodes together.
Preferably I will be able to rewire my generator 600V delta and only have to bond my generator container to my transformer container. (It is a Cummins so I may need a different pt/ct card in which case we won't be buying one and scraping the rewiring also I'm not quite sure if I need a computer program to tell the controller to expect a delta output rather than a wye etc.)
What would you suggest and is there anything above that is an incorrect method ie. bad grounding practice.
Appreciate all insight.
I have a 347/600V generator and I will be connecting it to a 600V/208V delta to wye transformer. I do not know what random loads are going to be connected to the transformer so I must assume I will end up with some unbalanced phases. Is it perfectly okay to connect only my phases to the transformer and leave my neutral floating, or should I tie the neutral within my generator to the generator ground. The secondary of my transformer will have a neutral to ground bond with my main electrode in the vicinity of my transformer secondary. I will not be installing any other electrode in the system and I will also have a bond connecting to every panel board the system supplies. (This is a temporary set-up for a field exercise)
If I leave the neutral floating I will run a bond from my gen container to the transformer.
If I bond my neutral to ground at the generator I will be installing an electrode at the generator and bond my two electrodes together.
Preferably I will be able to rewire my generator 600V delta and only have to bond my generator container to my transformer container. (It is a Cummins so I may need a different pt/ct card in which case we won't be buying one and scraping the rewiring also I'm not quite sure if I need a computer program to tell the controller to expect a delta output rather than a wye etc.)
What would you suggest and is there anything above that is an incorrect method ie. bad grounding practice.
Appreciate all insight.