Can you put a 35 amp fuse in a 30 amp disconnect if the disconnect supplies equipment with a 22 MCA and 35 MOCP?
But there are UL listing requirements. Fuses cannot be larger than the rated size of the switch or fuse holders, however, they can be smaller.Only if you have a big enough hammer
I do not know of a 30 amp rated disconnect that will physically accept a 35 amp fuse but there is no NEC requirement that you fuse must be equal to the max allowed.
But there are UL listing requirements. Fuses cannot be larger than the rated size of the switch or fuse holders, however, they can be smaller.
Yep. A 35A fuse is physically the size of a 60A one. It possibly wouldn't even fit into the enclosure, much less the fuse clips."Only if you have a big enough hammer"
I believe a 35 amp fuse is physically to big to fit in the fuse holders of a 30 amp disconnect.
Only if you have a big enough hammer![]()
But there are UL listing requirements. Fuses cannot be larger than the rated size of the switch or fuse holders, however, they can be smaller.
at least one manufacturer has a 35A class CC fuse that fits in a class CC (30A) fuse holder.
If you are thinking Littlefuse, who calls all of their CCMR fuses "Class CC" and says they go up to 60A, you might be mistaken. At 35-60A they are not the same size, so UL made them call them class CD. I think Littlefuse refers to them as class CC in the web page description because the current limiting capabilities are the same as the other CCMR series, but when you look at the data sheet they show a class CD for the larger ratings and they don't fit in the same fuse holder. I think it's a little misleading.at least one manufacturer has a 35A class CC fuse that fits in a class CC (30A) fuse holder.