Member
I'm a newbie to the forum and from my username you can safely assume that I'm a mechanical engineer with a very basic understanding of electricity. Recently we built a detached garage and I wanted a 200 amp panel in the new building, welders, compressors, car lift, heat and AC, etc..... The power company discouraged me from adding a new service and meter, and suggested coming off of the existing service as it would be cheaper. The house already had a 200 amp breaker panel served by an Alcan W 350 kcmil AL 600v 90c xlpe underground feeder (not in conduit and not a concentric ground) from a transformer located about 350 feet from the house. When the house was built 20 years ago the power company did not want to install a new transformer on our lot, so they buried a larger conductor instead to compensate for the distance (all utilities are under ground.) The new electrician has installed a 320 class meter base to replace the old one, and has run two separate 200 amp services off of it. One to feed the existing panel, and one to feed a new 200 amp disconnect, which now feeds the new 200 amp panel in the detached garage. My question is, is the power company's 350 kcmil feeder cable capable of supplying the total 400 amp load? I read that you really only get 80% or 320 amps from 400 amp service, but what can I truely expect from this installation as far as current draw at each panel? The new 200 amp panel is approximately 150 feet from the new discount and is fed by 4/0 AL conductor.