Couple questions regarding the Installation of the conductors for 1,216 ampmax standby generator(350kw) 120/208VAC
1) If I use PVC pipe on retaining wall distance of 200 feet from main service to generator i can put each phase isolated per conduit run? Can I run the ground and neutrals independently in its own conduit? I'm also confused about the ground size I interpreted the code as the size of the service which is 3,000amps?I dont want to do this but in terms of connecting to the terminals this may be easier. The size wire I would need would be if I use 3 conductors per pipe is 700kcm. If I run all 3 phases plus nuetral and ground in 1 pipe it would be 1,000kcm.
2) these conduits would pass behind the main transformer for the building. 2-3feet is the clearance to the wall I would be mounting the pipes on. I'm not sure the term to use for the magnetic field the transformer makes. Would this be a problem causing interference/heat to the back up generator? I believe this transformer would not be on when the power goes out and the generator kicks on.
1) If I use PVC pipe on retaining wall distance of 200 feet from main service to generator i can put each phase isolated per conduit run? Can I run the ground and neutrals independently in its own conduit? I'm also confused about the ground size I interpreted the code as the size of the service which is 3,000amps?I dont want to do this but in terms of connecting to the terminals this may be easier. The size wire I would need would be if I use 3 conductors per pipe is 700kcm. If I run all 3 phases plus nuetral and ground in 1 pipe it would be 1,000kcm.
2) these conduits would pass behind the main transformer for the building. 2-3feet is the clearance to the wall I would be mounting the pipes on. I'm not sure the term to use for the magnetic field the transformer makes. Would this be a problem causing interference/heat to the back up generator? I believe this transformer would not be on when the power goes out and the generator kicks on.