I got a fax from our PM today detailing what they wanted to do for an electrical service. The PDFs are too large to attach here, but I think I can sum up what they have for their single line. The are coming out of an existing wire way with a 200A 3 phase meter, than running into a 2 1/2" PVC conduit with (4) 250MCM Cu & (1) #2 GND. This breaks off into a 250A, 3 phase 4 wire panel with a 125A 3 phase 4 wire panel.
This alone is not bad, but what I put on the prints is a 400A meter with (4) 500 kcmil Cu W/ (1) 2/0 GND, running into a 4" conduit with (2) sets of (4) 3/0 Cu with (1) #4 GND, feeding into a wireway that branches off into two 200A panels.
The load calc the EC is showing is 76,756VA/359 Volts=213A @ 3ph 4 wire 208V
My load calc is 38,388VA+38,386VA=76,774VA/240 Volts=319.9A x 125%=399.9A
The EC's math works out, but I've never heard of a 359V service before. Is there some piece of the puzzle I don't have, or is the EC making up numbers to get his bid to be the lowest? Uh, you don't have to speculate on why, I just want to find out if there's a piece of the puzzle I'm missing.
This alone is not bad, but what I put on the prints is a 400A meter with (4) 500 kcmil Cu W/ (1) 2/0 GND, running into a 4" conduit with (2) sets of (4) 3/0 Cu with (1) #4 GND, feeding into a wireway that branches off into two 200A panels.
The load calc the EC is showing is 76,756VA/359 Volts=213A @ 3ph 4 wire 208V
My load calc is 38,388VA+38,386VA=76,774VA/240 Volts=319.9A x 125%=399.9A
The EC's math works out, but I've never heard of a 359V service before. Is there some piece of the puzzle I don't have, or is the EC making up numbers to get his bid to be the lowest? Uh, you don't have to speculate on why, I just want to find out if there's a piece of the puzzle I'm missing.