If the conductors are #4 and larger and the conduit body does not meet the requirements of 314.28, I would red tag it if it was used to reset the 360° rule.
 
Will a conduit body reset the 360 degree bend rule in lieu of a box? Thanks

Sometimes yes and sometimes no. Don gave you the no. For example if you're pulling 4-600 kcmil in a 3.5" EMT then a C conduit body isn't going to work for the 360° rule. It might help you to get the rope in the tubing. :)
 