Customers Upgrading to a 400 amp service to Install a 36kw Tankless unite and feed a work shop. It will be a 400 meter with 2-200 amp breakers feeding shop and house. I was thinking of Coming off the 200 amp that feeds the buss with a main lug kit. Then feed a 200 amp panel next to the tankless dedicated to it. Using the Optional method I get 138amp. so I could come off the house.
I don't feel comfortable with the deducts that it allows for the Tankless. He is using it to fill a 88 gallon claw tub. That takes a while to fill and some one could be doing clothes and cooking and trips the breaker. I was thinking of coming off the Shops 200 amp. I don't think to many people would be welding out side and using compressor and hot water at the same time but then again it can happen.
I don't really want to split them up between both 200 amps.
This is the first tankless I have done any thoughts?
I don't feel comfortable with the deducts that it allows for the Tankless. He is using it to fill a 88 gallon claw tub. That takes a while to fill and some one could be doing clothes and cooking and trips the breaker. I was thinking of coming off the Shops 200 amp. I don't think to many people would be welding out side and using compressor and hot water at the same time but then again it can happen.