380V/220V Machine Tool Transformer Grounding

Status
Not open for further replies.

Dale Hayes

Senior Member
I have a 380V Primary to 220V Secondary 250VA, 1-phase, Machine Tool Transformer powering a 220V control wiring. I have fused both the primary and the secondary side of the transformer.

My question: This is a 220V secondary. Can and should the X2 connection be grounded? Is grounding required at X2 when it is 220V?

Attached below is a forum on grounding Machine Tool Transformers dated 9-15-99.

Grounding - Machine Tool Transformers (9-15-99)

How and where should a dry type machine tool transformer with H1, H2, X1, and X2 terminals be grounded? Or, should it be left ungrounded? The transformers typically supply power to the components within the control panel but they also supply power to field-mounted loads and devices. These transformers are often enclosed in housing (some are of the open type) and the secondary voltage is generally 120V, but they can be 12V, 24V, 240V, and 480V.




Response No. 1

The transformer is automatically grounded when you screw the transformer housing to the control enclosure, which should be grounded. See the following Code Sections (1999 NEC) 250-112(d), 250-172, 250-178, 250-96(a)(b), 250-30, 430-96, 430-144, 450-10.




Also see NFPA 79, it has good information for your application and check with your manufacturer concerning this to verify. I hope this helps. I have a book on control transformers that shows this application.

David R. Carpenter, integrityco@mindspring.com




Member Comment

Response No. 1 is wrong. You must ground one side of the secondary otherwise it will not recognize the ground because a transformer is a floating coil and it needs to be bonded to ground to complete the circuit or you will get weird volt readings as indicated in Response No. 2.


Response No. 2

I have a lot of these transformers in my fish processing plant. We provide a jumper from X2 to the main ground on the control panel. If you don't ground the control transformer you can't trouble shoot the component parts because you'll get a bunch of weird voltage readings.
marktsmith@webtv.net




Response No. 3

Machine tool wiring is not required to comply with the NEC because the components if the wiring is designed by an engineer who accepts the liability for the system. Not all machine tool transformers are or should be grounded. You need to check with the wiring schematics for the machine you are installing it in. If it shows the secondary side grounded, it will generally be grounded at X2. However some control systems have been designed to be ungrounded to protect them from stray currents, or other types of interference, and grounding them would not only be a bad idea, it would violate the listing of the machine.




If you can't tell by looking at the schematics whether grounding is appropriate or not I would suggest you call the manufacturer and talk to their service department. Usually this kind of question is very welcome as it can save a lot of trouble later on when the wrong procedure is followed. You should never change the designed wiring because to do so sets you up to be liable for the system.

Michael White, Mwhite2690@aol.com




Response No. 4

I always grounded the X2 connection. This stabilized the control voltage for these installations.

Joseph Wages Jr., jwages@admin1.siloamsprings.com




Response No. 5

Generally since there is 120v potential between X1 and X2 on the secondary, X2 is used as the secondary grounded conductor, and equipment ground. Let me know if I am wrong. This is the way we wire our alarm panels, and secondary contact voltage on motor starters.

Ken Teverbaugh, kbcjkt@worldnet.att.net




Mike Holt?s Response

The purpose of grounding is to remove dangerous voltage from metal parts of the electrical system and/or building structure that occurs during a ground-fault. Failure to remove the dangerous voltage can create a condition where persons can be killed by electric shock and/or fire, not to mention power quality issues.




To remove dangerous voltage from metal parts, the circuit overcurrent protection device must open to clear the ground-fault. The effectiveness of the grounding path plays a vital role in the activation of the overcurrent protection device to clear the ground-fault. To open the protection device quickly, the impedance of the grounding path must be low enough to permit ground-fault current to reach a level of at least 3 times (preferably 5-10 times) the overcurrent protection device?s rating.




This is accomplished by bonding the metal parts to the system?s grounded conductor (X2), which provides the low impedance path necessary to facilitate the clearing of phase-to-ground faults by opening the circuit overcurrent protection device.




However NEC Section 250-20 states that alternating-current circuits of less than 50 volts must be grounded under any of the following conditions:

1. If the transformer supply system exceeds 150 volts to ground

2. If the transformer supply system is ungrounded

3. Where installed as overhead conductors outside of buildings




So the bottom line is unless it?s designed by an electrical engineer, ground all systems that operate at over 50 volts by bonding the X2 terminal to the grounded metal enclosure.
 
Grounding Control Xfmr Secondary

Grounding Control Xfmr Secondary

I have a 380V Primary to 220V Secondary 250VA, 1-phase, Machine Tool Transformer powering a 220V control wiring. I have fused both the primary and the secondary side of the transformer.

My question: This is a 220V secondary. Can and should the X2 connection be grounded? Is grounding required at X2 when it is 220V?

QUOTE]

Yes,Yes,No(If electrical engineer design does not require X2 to be grounded for some reason). When you ground X2 be sure to follow the requirements of 430.74 with respect to the grounded conductors arrangement in your control wiring.
 
081126-2031 EST

In the past machine control logic using relays was wired with the secondary ungrounded. Ground fault lights were provided to indicate a short to ground. This did not present a safety problem because the machine, its enclosures, and all non-control circuit conductive surfaces were grounded. This included the transformer enclosure, frame and laminations. The primaries were generally supplied from a floating delta and therefore not grounded.

When the control wiring shorted to ground, machine frame, etc., one of the lights would get bright, but the machine function might not be affected. Important in a high volume production application. A single short to ground would be no real problem. Two different shorts to ground would probably cause a machine malfunction.

With the evolution to PLC control the trend has been to grounding one side of the control transformer secondary. This trend I believe was to reduce noise problems.

There are probably still some relay logic control machines with floating secondaries in use.

.
 
081126-2031 EST

In the past machine control logic using relays was wired with the secondary ungrounded. Ground fault lights were provided to indicate a short to ground. This did not present a safety problem because the machine, its enclosures, and all non-control circuit conductive surfaces were grounded. This included the transformer enclosure, frame and laminations. The primaries were generally supplied from a floating delta and therefore not grounded.

When the control wiring shorted to ground, machine frame, etc., one of the lights would get bright, but the machine function might not be affected. Important in a high volume production application. A single short to ground would be no real problem. Two different shorts to ground would probably cause a machine malfunction.

With the evolution to PLC control the trend has been to grounding one side of the control transformer secondary. This trend I believe was to reduce noise problems.

There are probably still some relay logic control machines with floating secondaries in use.

.

It should be grounded.

I don't believe that the information supplied above is sufficient to apply to the Code exception for ungrounded supply.
 
I believe most of the responses are so much malarky.

The NEC does not require control circuits to be grounded. read carefully what is required to be grounded.

250.20 Alternating-Current Systems to Be Grounded.
Alternating-current systems shall be grounded as provided for
in 250.20(A), (B), (C), or (D). Other systems shall be permitted
to be grounded. If such systems are grounded, they shall
comply with the applicable provisions of this article.
...
(B) Alternating-Current Systems of 50 Volts to 1000
Volts. Alternating-current systems of 50 volts to 1000 volts
that supply premises wiring and premises wiring systems

shall be grounded under any of the following conditions:

A control transformer does not supply premises wiring or premises wiring systems.
 
The NEC does not require control circuits to be grounded. read carefully what is required to be grounded.
A control transformer does not supply premises wiring or premises wiring systems.
Bob,
Are you sure? Take a look at the Article 100 definition of premises wiring. It is very inclusive and about the only thing that is not premises wiring is wiring that remains completely with in the equipment. Maybe that is the case here, but many control circuits extend beyond the equipment and are premises wiring.
Premises Wiring (System). Interior and exterior wiring, including power, lighting, control, and signal circuit wiring together with all their associated hardware, fittings, and wiring devices, both permanently and temporarily installed. This includes (a) wiring from the service point or power source to the outlets or (b) wiring from and including the power source to the outlets where there is no service point.
Such wiring does not include wiring internal to appliances, luminaires, motors, controllers, motor control centers, and similar equipment.
 
Bob,
Are you sure? Take a look at the Article 100 definition of premises wiring. It is very inclusive and about the only thing that is not premises wiring is wiring that remains completely with in the equipment. Maybe that is the case here, but many control circuits extend beyond the equipment and are premises wiring.

I yet have to see an MCC combination starter with integral control transformer where X2 is not grounded.
 
Section 8.3 of NFPA 79 states that the control circuit can be either grounded or ungrounded within the machine.

If ungrounded it must be monitored if above class 2.
Or if exposed it must be grounded.
 
I yet have to see an MCC combination starter with integral control transformer where X2 is not grounded.
I have worked on a number of them and the first thing I do when I troubleshoot the control circuit is make a temporary grounding connection on X2.
 