cripple
Senior Member
- Location
- Santa Fe, New Mexico
Section 300.15 clearly requires a box or conduit body for all cable systems at each conductor splice point, outlet point, switch point, junction point, termination point, or pull point, unless otherwise permitted in 300.15(A) through (L). All wiring methods in chapter 3 without a removable cover require a box or refer you back to 300.15. Section 90.3 states that the first 4 chapters apply generally and chapters 5, 6, and 7 supplement or modify the general rules.
My question is why is it, that section 392.56 permit splicing of cables in cable tray without using box or conduit body. Section 392.56 has no reference to 110.14 or 300.15. I know that cable tray is not a wiring method and is defined as a structural system used to securely fasten or support cables and raceways systems. Since cable tray requirements are located in chapter 3 it should not modify the general rule or is there something I'm over looking or not grasping.
My question is why is it, that section 392.56 permit splicing of cables in cable tray without using box or conduit body. Section 392.56 has no reference to 110.14 or 300.15. I know that cable tray is not a wiring method and is defined as a structural system used to securely fasten or support cables and raceways systems. Since cable tray requirements are located in chapter 3 it should not modify the general rule or is there something I'm over looking or not grasping.