392.80(A)(2)(D) Doubt, this is correct?

Merry Christmas
Status
Not open for further replies.

Emiliano

Member
Location
México
Occupation
Electrical Engineer
1691169540117.png
Hello everyone, Acoording to NEC articulo 392.80(A)(2)(D), "where single conductors are installed in a triangular or square configuration in uncovered cable trays, with a maintained free airspace not less tha 2.15 times one conductor diameter of the largest conductor contained of the adjacent conductor configurations or cables, the ampacity of 1/0 AWG and larger cables shall not exceed the allowable ampacities of two or three single conductors rated 0 through 2000 volts supported on a messenger in accordance with 310-.15 (B), see table 310.15(B)(20)"

so my doubt is: in this kind of arragment we take the ampacity of two or three conductors only?
for example: the total ampacity of the circuit is 2900A or 1740A? taking 310.15(B)(20) table.


imagen.png
 
The ampacity is 2900 however that is at 90°C. You would have to make sure your equipment is rated the 90°C ampacity. In addition the rules in 110.14 will limit the terminations to the ampacities found in Table 310.15(B)(16) unless the equipment is marked otherwise.
 