392.12 & 392.13 High Voltage.
392.12 gives Impression cable tray must be sized by dia. od conductors laying side by side.
750 unshielded copper 5 kv=1.62 Dia. 18x1.62=29.16 = min 30 inch tray.
Ampacitys of cable (single conductor) 392.13(b)
#1 = Side by side no spacing 310.69 uncovered 75%.
Covered over 6 feet 70% of the table.
#2 Single row one conductor space between Ampacity Table 310.69 100%.
#3 Cables Bundled 3 in a bundle (a-b-c)and a space between of 2.15x conductor size.= 100% of table 310.67.
Question can bundles be put side by side?? if so ampacity??? If so can tray be Sized by width of cables side by side. 1.62x2=3.24x6(bundles)=19.44
say a 24 inch tray.
I feel min tray size 30 inches(392.12). Cables must be installed per 392.13(B) 1 ,2, or 3.
Any Imput >???
say a 24 inch tray.
Any Imput >???