3p/4w 120/240 delta w/208 high leg

Status
Not open for further replies.

booter

Member
I work for an electric utility in Texs. In a recent conversation with a coworker, he made a comment that I found to be untrue.
We were talking about an upcoming job involving the installation of a 3 phase/4 wire, 120/240 w/208 high leg, delta service. We have long been encouraging customers to accept 3 phase/4 wire, 120/208 wye services to better keep our primary distribution system balanced. This coworker commented that the electricians here are balancing what they can on the 4 wire delta services by taking the 208v(high phase) and a 120v phase to a single phase 240v appliance(hot water heater,etc.) rather than both 120v phases to produce 240v. I said that I had never seen that done and that the only high leg load I had ever seen was associated with three phase load.
I also question whether it is acceptable according to NEC to use the high leg in this manner. Any comments would be appreciated.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Re: 3p/4w 120/240 delta w/208 high leg

I have always used the high leg in any phase to phase single phase loads.

Do not confuse these 240 V loads with 120/240 V loads such as a dryer, which would utilize a "neutral" connection.

FPN: Most do not consider the grounded conductor of a delta a neutral. :)

Roger
 

charlie

Senior Member
Location
Indianapolis
Re: 3p/4w 120/240 delta w/208 high leg

Booter, it is common for the EC to make use of the B phase by going from either A or C phase to the B phase (higher phase to ground). This is legal and recommended so the panelboard may be more completely utilized. See Roger's post for more information. A 120/240 volt, 3 phase, 4 wire panelboard would have all the 3 phase slots filled with 3 phase circuit breakers then a blank for every 3rd slot if it wasn't done this way.

Electric utility engineers will usually ask for the loads broken into 1 phase and 3 phase for sizing their service drops and transformers. This method doesn't work! See above for the reason. :D

BTW, what do you do for the utility?
 

BAHTAH

Senior Member
Location
United States
Re: 3p/4w 120/240 delta w/208 high leg

Booter, What your co-worker describes is a common application. This is one reason for the Slash rating of circuit breakers such as 120/240V for use one circuits where the phase to phase voltage does not exceed 240V and the phase to neutral or gcc does not exceed 120v. A 240v rated breaker would be required for connection on a circuit that is phase to phase 240v only with no gcc. Generally if you order a panelboard with a specified breaker layout the manufacture will block the bus at all b-phase positions that are not utilized for 2 or 3-pole breakers, on loadcenters it is up to the installer to properly install the panel with respect to the use of b-phase.
 