New to these forums, hello!
I running an arc flash study for a large industrial plant. I am using the Edsa Technical 2005 software to model the system and determine the arc flash categories and available sc / clearing times for specific feeders. When I ran the study I found that some feeds are protected very poorly and some protective devices take a very long time to trip, or do not trip at all to clear a fault. These usually are downstream of step down transformers.
My question is if the fault happens for a very long time (ie over 10 secs) is there a point where you should cut it off? For the purpose of determining the arc flash category. The problem is if the fault last for a very long time, even small arc flash energy over a very long time drives the arc flash category way up. Where do you draw the line?
I running an arc flash study for a large industrial plant. I am using the Edsa Technical 2005 software to model the system and determine the arc flash categories and available sc / clearing times for specific feeders. When I ran the study I found that some feeds are protected very poorly and some protective devices take a very long time to trip, or do not trip at all to clear a fault. These usually are downstream of step down transformers.
My question is if the fault happens for a very long time (ie over 10 secs) is there a point where you should cut it off? For the purpose of determining the arc flash category. The problem is if the fault last for a very long time, even small arc flash energy over a very long time drives the arc flash category way up. Where do you draw the line?