Hey y'all, I've got a customer who's building formerly had a 3ph 240v high leg delta service fed from 3 pole mounted transformers (Two 15kva and one 25kva). They're the only customers on this bank. At some point the building switched to a single phase 240/120 (it's complicated). Now, there's new owners renovating for a new business, and they're looking to get a 3ph service, 39kva load.
The utility won't provide a high leg delta anymore, and originally said I can't get a wye service at all. Now they're saying I can, but I might have to upgrade the transformer. I'm not all that familiar with the utility side of things, so I'm not really sure why that would be the case. Seems to me like it's a pretty simple reconfiguration, and the transformers should be sized appropriately.
The utility reps haven't seemed like they've spent a ton of time actually looking at the situation, but again, I don't really know what the utility is taking into consideration here, so maybe I'm missing something?
The utility won't provide a high leg delta anymore, and originally said I can't get a wye service at all. Now they're saying I can, but I might have to upgrade the transformer. I'm not all that familiar with the utility side of things, so I'm not really sure why that would be the case. Seems to me like it's a pretty simple reconfiguration, and the transformers should be sized appropriately.