3ph-3w vs 3ph-4w

Status
Not open for further replies.

Designer69

Senior Member
why do you sometimes need to run a neutral to a 3 phase load?

IE, a 3 phase air compressor with a control panel, design shown is 4 pwr and 1 gnd.

Thanks
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
why do you sometimes need to run a neutral to a 3 phase load?

IE, a 3 phase air compressor with a control panel, design shown is 4 pwr and 1 gnd.

Thanks

Only if they are using the neutral for something. For example in some 208V panels, they use 120V controls by connecting L-N rather than use a Control Power Transformer. A 3 phase motor doesn’t care though.
 

adamscb

Senior Member
Location
USA
Occupation
EE
If a load is three-phase, then all line currents should be equal, and therefore no current travels on the neutral. If a panel is 3ph-3w then it can't serve single-phase loads. If it's 3ph-4w then it can serve single-phase loads.
 

smoothops10

Member
Location
FL
Occupation
EE
Both good responses but keep in mind I believe NFPA 79 requires the CPT be less than 1000 VA to limit short circuit current available to the 120V control pilot devices and relays. Probably only a real factor if the control panel is real close to the source but in general I've defaulted to specifying all 208V 3 phae controls panels as 3W+G w/ CPT in lieu of 4W+G w/o CPT so I don't have to worry about it. Unbalance due to a 50 or 150 VA CPT is generally negligible and can be ignored.
 

kwired

Electron manager
Location
NE Nebraska
If a load is three-phase, then all line currents should be equal, and therefore no current travels on the neutral. If a panel is 3ph-3w then it can't serve single-phase loads. If it's 3ph-4w then it can serve single-phase loads.
If load is three phase only there isn't even a neutral conductor on the load to connect to.

A 3 ph-3w source can supply single phase loads - they will have to be line to line and not line to neutral (ie. 208 volts and not 120).
 

smoothops10

Member
Location
FL
Occupation
EE
Again NFPA 79 I believe limits control voltage to max 120V or 200V nominal. I don't have it it in front of me but from what i recall utilizing 208V LL single phase for pilot control ckts would not be allowed if building to this standard.
 

adamscb

Senior Member
Location
USA
Occupation
EE
If load is three phase only there isn't even a neutral conductor on the load to connect to.

A 3 ph-3w source can supply single phase loads - they will have to be line to line and not line to neutral (ie. 208 volts and not 120).

Yes k-wired, you are right, thanks for clarifying. Should have said it can't supply L-N loads.
 