50 gallon heater3500/480/1.73=4.2 amps. 15 amp circuit. I'm surprised that such a small heater is 3 phase.
Just out of curiosity do you have a part number?50 gallon heater
Use the smallest breaker you can get, then put a fused disconnect at the water heater.A 3,500 watt heating element feed from 480 volts three phase would draw approximately 4.207 amps. So a 15 amp circuit breaker would easily handle it. I never came across a 6,7 or 10 amp three pole circuit breaker that would fit into conventional 480 volt three phase panels. I used to use a cheater multiplier for ruff field three phase 480 volt calculations by multiplying the KW by 1.2 . example 3.5 KW × 1.2 =4.2 Amps.
Why would you need a fused disconnect?Use the smallest breaker you can get, then put a fused disconnect at the water heater.
I case it required protection less than the smaller breaker you could use. If it can use a MOCP device of 15A then it wouldn't be required.Why would you need a fused disconnect?
I case it required protection less than the smaller breaker you could use. If it can use a MOCP device of 15A then it wouldn't be required.