Hi All,
I'm trying to figure out what happened with some transformers and hope someone has seen something similar before:
Problem: All three Xfmr (5KVA each) Bank will blow a fuse when hooked up to 480VAC three phase. The customer reported that when power was applied (input fused switch closed) that two of the three line fuses would blow immediately. These are Acme 240/120 general purpose xfmrs. Primary: Ph1 to H1,H5 and Ph2 to H2,H6. Secondary: X1(Hot), X4(Neutral), X2/X3 connected. I haven't gotten far enough to see if these connections actually produce the desired Voltages or not. In summary, two of 6 primary windings are energized with a full secondary.
Background: Transformer bank was built in Alaska years ago to step down 480VAC to two outputs: 380VAC Delta and 220VAC WYE to run some IEC Euro Equip. Rumor (no personal observation) has it that it ran good once. Not anymore. I think their thinking on how to transfer euro equip to run in the US is faulted, and i've given them some better suggestions, but I was paid to make the transformers produced the Euro voltages at 60Hz. That part sounded easy to me on something that has worked before.
Ok, so what did I do:
I lifted leads on the primaries and secondaries and supplied 480VAC to input terminals, no xfmrs on line, to check the input pwr cord and input pwr fused switch, no problems noted. Meggared all three primaries and got a little less than an Ohm on each. Meggared the secondaries and got a little less than an ohm on each as well. Pri and Sec to ground was greater than 40 MOhm. Pri to the sec was greater than 40 MOhm. So far so good. I kept the secondary leads lifted and taped and one by one applied power to the primaries. No go. Each time the input Fuse (one of the two powering the transformer) (FRS-r-10A) blew immediately. All three transformers had the same readings, indications and all blew the fuse immediately. I just can't believe that 3 xfmrs would all go bad at the same time.
What is confusing me is that I am sure that I have short somewhere in the equipment but cannot find it with test equipment. Also, the probability that a transformer could go bad is always there but three transformers with exactly the same indications? The odds on that one are small.
I'm going back tomorrow morning. My plan is to open the leads at each tranformer, pwr the primaries directly with a new wire straight from the generator -> fused switch -> new wire directly to the xfmr and measure volt across the secondaries (x1 to x4). If it blows after I've removed all equipment and existing wiring... it has to be bad. I would just hate to tell the customer he has 3 bad xfmrs when I cannot show them as bad with test equipment or explain how three went bad at the same time.
I'm positive I'm missing something and just don't know what. Help or suggestions would be appreciated?
John King
I'm trying to figure out what happened with some transformers and hope someone has seen something similar before:
Problem: All three Xfmr (5KVA each) Bank will blow a fuse when hooked up to 480VAC three phase. The customer reported that when power was applied (input fused switch closed) that two of the three line fuses would blow immediately. These are Acme 240/120 general purpose xfmrs. Primary: Ph1 to H1,H5 and Ph2 to H2,H6. Secondary: X1(Hot), X4(Neutral), X2/X3 connected. I haven't gotten far enough to see if these connections actually produce the desired Voltages or not. In summary, two of 6 primary windings are energized with a full secondary.
Background: Transformer bank was built in Alaska years ago to step down 480VAC to two outputs: 380VAC Delta and 220VAC WYE to run some IEC Euro Equip. Rumor (no personal observation) has it that it ran good once. Not anymore. I think their thinking on how to transfer euro equip to run in the US is faulted, and i've given them some better suggestions, but I was paid to make the transformers produced the Euro voltages at 60Hz. That part sounded easy to me on something that has worked before.
Ok, so what did I do:
I lifted leads on the primaries and secondaries and supplied 480VAC to input terminals, no xfmrs on line, to check the input pwr cord and input pwr fused switch, no problems noted. Meggared all three primaries and got a little less than an Ohm on each. Meggared the secondaries and got a little less than an ohm on each as well. Pri and Sec to ground was greater than 40 MOhm. Pri to the sec was greater than 40 MOhm. So far so good. I kept the secondary leads lifted and taped and one by one applied power to the primaries. No go. Each time the input Fuse (one of the two powering the transformer) (FRS-r-10A) blew immediately. All three transformers had the same readings, indications and all blew the fuse immediately. I just can't believe that 3 xfmrs would all go bad at the same time.
What is confusing me is that I am sure that I have short somewhere in the equipment but cannot find it with test equipment. Also, the probability that a transformer could go bad is always there but three transformers with exactly the same indications? The odds on that one are small.
I'm going back tomorrow morning. My plan is to open the leads at each tranformer, pwr the primaries directly with a new wire straight from the generator -> fused switch -> new wire directly to the xfmr and measure volt across the secondaries (x1 to x4). If it blows after I've removed all equipment and existing wiring... it has to be bad. I would just hate to tell the customer he has 3 bad xfmrs when I cannot show them as bad with test equipment or explain how three went bad at the same time.
I'm positive I'm missing something and just don't know what. Help or suggestions would be appreciated?
John King